Correct. My place has 200amp service and the previous owners had an sauna I use as a cedar closet. Just took that location on the panel. Sauna in Florida is going outside.I think it's 40A continuous requires a 50A circuit, and 48A continuous requires a 60A circuit. 125% of load (or 80% continuous on circuit)
My electrician said that outlets have melted and burned due to the constant draw of power.Is it worth it to spend the extra money for 8 more amps of charging current (40a with plug vs. 48a hardwired)?
NEVER wire a 14-50 to a 60A circuit. The 80% rule applies to the 14-50 too. So, no higher than a 50A breaker for a 50A outlet, and the max continuous load should never be higher than 40A. Putting this on a 60A breaker, and expecting it to run 48A through the outlet is just asking for the outlet to melt.You should spend a minute watching Tom on the YouTube Channel: Star of Charge.
He has spent nearly 10 years testing and reporting on chargers.
For maximum Level 2 charging you will need a 60 amp/240v circuit w a 14-50 receptacle. Most all the current chargers that 40-48Amp level 2 can be hardwired for 48amps and have 14-50 plugs for 40amps. Hardwiring will be more expensive then having a heavy duty cycle (EVSE rated) plug installed.
State of Charge will help you with your knowledge and give you a ton of reviews of the many different chargers out there.
That is what we did. We have two EV’s (no more ICE for us) and <15 mile round trip commutes and we just did a 14-50 Nema plug and use the charger that came with one of the cars with its 240 adapter. Can easily recharge from pretty low to full overnight on the rare occasion that’s needed.I'm planning on (mostly) charging my Slate from home, and I was going to have a 240V outlet installed in the carport of my mobile home.
Can I spare the expense of a dedicated charger and just have a heavy duty 240V outlet installed?
Also, do I need to check amperage requirements? I live in a mobile home built when disco was king.
Thanks for the education-
And a new electrical code just went into effect; the breaker must be GFCI type!NEVER wire a 14-50 to a 60A circuit. The 80% rule applies to the 14-50 too. So, no higher than a 50A breaker for a 50A outlet, and the max continuous load should never be higher than 40A. Putting this on a 60A breaker, and expecting it to run 48A through the outlet is just asking for the outlet to melt.
If you want a 60A breaker and charge at 48A, then hardwire is the way to go.
Makes no sense when the EVSE itself is a GFCI. Likely this for non-hard wired installationsAnd a new electrical code just went into effect; the breaker must be GFCI type!
Correct.Makes no sense when the EVSE itself is a GFCI. Likely this for non-hard wired installations